[Pumptesting] Fw: Re: Fw: Pump Test Failure?
Phéna Proxima
adam at phenaproxima.net
Tue Aug 5 12:12:01 EDT 2025
Update from Daver on the sensor issue:
> No need for Encore. What happened is that the waterflow sensor for the building's own sprinkler system tripped. The waterflow sensor is near the test valve. If there's a lot of turbulence in the pipes, that can fool the sensor into thinking there's water flowing. Opening the test valve wide open can make this more likely.
>
> It doesn't mean there's anything wrong. Just keep lowering the pressure until it gets to 80 PSI and the main pump turns on.
-------------- next part --------------