System on TEST until 8pm; Daver is back up alarm watch until 8 so Tara can go offsite.<div dir="auto"><br></div><div dir="auto">Ongoing: Generator for fire pump side still awaiting repair.</div><div dir="auto"><br></div><div dir="auto">On arrival at 90, Cistern level display was off; turned out wall power through transformer never reconnected to box after sensor swap.</div><div dir="auto"><br></div><div dir="auto">Put system on test, then plugged back in to charge. No change. After ~5-10 minutes, swapped for different battery. </div><div dir="auto"><br></div><div dir="auto">Panel worked, level reported 6.6, threshold for “FILL” correctly triggered, solenoid valve opened and audibly filling. Level at 6.9 by the time we left, fresh water unphased at 5.0’. Booster 2 was running as Lead. FW steady at 50psi while cistern filling.</div><div dir="auto"><br></div><div dir="auto">No transfer switch tests performed.</div>