[Pumptesting] 10/25 pump test Completed, Mike will do next one (with Tara); battery issue found and resolved
Tara Halwes
tarahalwes at gmail.com
Sat Oct 25 19:49:05 EDT 2025
System on TEST until 8pm; Daver is back up alarm watch until 8 so Tara can
go offsite.
Ongoing: Generator for fire pump side still awaiting repair.
On arrival at 90, Cistern level display was off; turned out wall power
through transformer never reconnected to box after sensor swap.
Put system on test, then plugged back in to charge. No change. After ~5-10
minutes, swapped for different battery.
Panel worked, level reported 6.6, threshold for “FILL” correctly triggered,
solenoid valve opened and audibly filling. Level at 6.9 by the time we
left, fresh water unphased at 5.0’. Booster 2 was running as Lead. FW
steady at 50psi while cistern filling.
No transfer switch tests performed.